    Default Delaval 78 on 7000 generator

    Just setting up a 78 with a 7000 watt gen. It wont quite kick over and run full speed. It starts smoking. I'm using 10 ga wire cuz the gen. Is only 10 feet away. Is that not heavy duty enough? Any suggestions? Thank alot!
    Last edited by Asa Matras; 02-07-2020 at 12:41 PM.
    Matras Maple

    Started 15 years ago as backyard operation.
    Now have a 1325 taps and growing.
    Boiling on a 2.5x8 leader infurno with steamaway.
    New for 2019 a cdl 600 expandable RO, another bush on vac.

  2. #2
    Join Date
    Nov 2018
    Location
    Franklin, PA
    Posts
    44

    Default

    Quote Originally Posted by Asa Matras View Post
    Just setting up a 78 with a 7000 watt gen. It wont quite kick over and run full speed. It starts smoking. I'm using 10 ga wire cuz the gen. Is only 10 feet away. Is that not heavy duty enough? Any suggestions? Thank alot!
    what size motor? does it say on the spec plate how many amps it draws at a given voltage?
    2019 290 taps on 3/16"
    2018 20 taps on milk jugs
    2017 10 taps on milk jugs

  3. #3
    Join Date
    Apr 2017
    Location
    Pittsfield, NH
    Posts
    76

    Default

    It's a 5 hp motor. FLA is 19.5 amps
    Matras Maple

    Started 15 years ago as backyard operation.
    Now have a 1325 taps and growing.
    Boiling on a 2.5x8 leader infurno with steamaway.
    New for 2019 a cdl 600 expandable RO, another bush on vac.

  4. #4
    Join Date
    Mar 2009
    Location
    North Augusta
    Posts
    97

    Default

    From what your telling me a 7000 watt gen set trying to kick start a 5 hp motor? You have an Under powered generator. Pretty sure even a 10k gen set won’t kick over the 78k. I tried the same route with a 76 and. 3 hp motor and it wouldn’t work. I ended up putting a 5.5 hp Honda to drive the 76. Works like a charm.

    I was running 10 gauge wire from the ten set to the motor, gave up o it and went to direct drive

    Hope you figure something g out for it
    Powered by oil fired 3X8 Lapierre cooker
    1478 taps
    330 GPH RO
    H20 Auto Drawoff
    10" cdl Filter Press
    2 adult kids
    Dog
    "memories of the old way"
    Kioti CK27
    Www.halladaymaple.ca

  5. #5
    Join Date
    Mar 2012
    Location
    Walpole, NH
    Posts
    1,363

    Default

    Quote Originally Posted by Asa Matras View Post
    It's a 5 hp motor. FLA is 19.5 amps
    Starting amps will be much higher. Takes a lot of umph to start a 5hp motor.
    Sugaring for 45+ years
    New Sugarhouse 14'x32'
    New to Me Algier 2'x8' wood fired evaporator
    2022 added a used RB25 RO Bucket
    250 mostly Sugar Maples, 15% Soft Maples. Currently,(110on 3/16" and 125 on Shurflo 4008 vacuum, 15 gravity), (16,000 before being disabled)
    1947 Farmall H and Wagon with gathering tank
    2012 Kubota with forks to move wood around

  6. #6
    Join Date
    Nov 2018
    Location
    Franklin, PA
    Posts
    44

    Default

    For 19 amps, you only need 12 gauge wire
    I realize there will be a starting spike, but that’s momentary. So you’re more than good with 10ga
    Ignore the post above saying your generator isn’t big enough. 7000 watt generator will push nearly 60 amps at 120.

    Just to be clear, what is smoking? The pump or the generator?
    2019 290 taps on 3/16"
    2018 20 taps on milk jugs
    2017 10 taps on milk jugs

  7. #7
    Join Date
    Mar 2010
    Location
    Morrisville, VT
    Posts
    88

    Default

    I have a 78 and I'm running it with an 18hp gas motor. There's a big "lug" when it kicks it on. I'd look at using a contactor or a variable drive. I'm curious as well, what is smoking?
    King 2x6 with Steam-Away
    16x34 Sugarhouse
    460 on Vac
    I thot this was supposed to be a hobby

  8. #8
    Join Date
    Feb 2010
    Location
    Leeds County,Ontario,Canada
    Posts
    1,038

    Default

    I have a De Laval 76 pump with a 3 hp motor,tried a 8750/7000 watt generator from Sam’s Club,didn’t have the oomph to run it,too much to start. Now I have a 12000 watt generator,fits the bill with 10 gauge wire. Sometimes on colder days I have to start it with valves open until it gets up to speed,have even had to slip belts off occasionally to just run the motor until it warms up,but that is pretty rare. You could try starting it if you have a way of allowing lots of air in so that it is not trying to build vacuum until it is up and running.
    7th generation maple producer in sugarhouse built in 1892
    2x World Champion Maple Syrup Producer
    1250 taps on cv adapters
    Leader Vortex 3x14 with Max Flue and Revolution Syrup Pan,Enhanced Steam Away
    www.leggettmaplesyrup.com

  9. #9
    Join Date
    Mar 2012
    Location
    Walpole, NH
    Posts
    1,363

    Default

    Quote Originally Posted by iby View Post
    For 19 amps, you only need 12 gauge wire
    I realize there will be a starting spike, but that’s momentary. So you’re more than good with 10ga
    Ignore the post above saying your generator isn’t big enough. 7000 watt generator will push nearly 60 amps at 120.

    Just to be clear, what is smoking? The pump or the generator?
    Starting a cold 78 pump with 5hp motor takes a lot more than your normal 19 amp draw. Have years of experience with them and you need good power to start them.
    Sugaring for 45+ years
    New Sugarhouse 14'x32'
    New to Me Algier 2'x8' wood fired evaporator
    2022 added a used RB25 RO Bucket
    250 mostly Sugar Maples, 15% Soft Maples. Currently,(110on 3/16" and 125 on Shurflo 4008 vacuum, 15 gravity), (16,000 before being disabled)
    1947 Farmall H and Wagon with gathering tank
    2012 Kubota with forks to move wood around

  10. #10
    Join Date
    May 2010
    Location
    Berne N.Y.
    Posts
    198

    Default

    A motor is an inductive load VS a heater as a resistive load. A 5HP motor will draw 100's of amps on inrush "start-up". A resistive "heater" load will only typically draw name plate amps. This is why it seems the generator should run it but it won't.
    2.5X10 HE
    600 RO
    Vac

+ Reply to Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts