Thread: Electricians, am I missing something??

  1. #1
    Join Date
    Mar 2016
    Location
    Winter, Wisconsin
    Posts
    138

    Default Electricians, am I missing something??

    I have a small transfer pump (115v / 1.8 amp) and a generator (120v / 1800 watts). I cannot power the pump off the generator???. Since it had been a while since I used the generator, brought it back to the shop, plugged a grinder (120v / 6 amp) into it, worked fine. So then thinking the pump was bad, brought it back to the shop, plugged into wall outlet and worked fine... I thought 110, 115, and 120 were, for all intent and purposes, the same??

  2. #2
    Join Date
    Mar 2015
    Location
    Alcona County, Michigan
    Posts
    1,134

    Default

    The starting current of a motor can be as much as 13 times the full load amps of the motor and that can kick the snot out of a generator. Pumps take longer than many other motors to come up to full speed and they essentially look like a short circuit to the power supply until they do. I'm guessing that your generator just hates your pump.
    CE
    44° 41′ 3″ N

    2019 -- 44 Red Maples - My home and sugarbush are for sale.
    2018 -- 48 Red Maples, 7 gallons
    2017 -- 84 Red Maples, 1 Sugar Maple, and 1 Silver Maple , 13 gallons
    2016 -- 55 Red Maples, 8 gallons
    2015 -- 15 Red Maples, 6 Birches - 3+ gallons maple syrup
    An awning over my deck is my sugar shack.
    An electrified kitchen sink and an electrified steam table pan are my evaporators.

  3. #3
    Join Date
    Mar 2016
    Location
    Winter, Wisconsin
    Posts
    138

    Default

    Quote Originally Posted by Cedar Eater View Post
    The starting current of a motor can be as much as 13 times the full load amps of the motor and that can kick the snot out of a generator. Pumps take longer than many other motors to come up to full speed and they essentially look like a short circuit to the power supply until they do. I'm guessing that your generator just hates your pump.
    The pump isnt even trying to move, it's not even loading the generator. Agree that my generator does t like the pump but, the start up of the pump is less than the grinder that worked fine.

  4. #4
    Join Date
    Jan 2011
    Location
    Poultney VT
    Posts
    2,420

    Default

    If the generator is starting the saw at 720W no problem, I'm thinking the cord on the pump has an issue. Even though you p;lugged it into the wall outlet and it worked fine. plug it in again and wiggle the cord at the outlet and where it goes into the motor housing of the pump. Also if you have a volt meter check how many volts at the generator when idling.

    As a general rule of thumb motors can go over by 10% and under by 5% of rated voltage and still work fine.
    Business Name
    Flat Lander Sugaring (who would think a guy from Az be making syrup)
    125 on Sap Suckers
    Close to 475 High Vac
    400 gravity adding more
    leader 2x6
    home made preheater
    hoods
    1 7D749 for AOF
    New FLS Tsunami Arch
    4 membrane TR Industries RO 2HP 3 phase 601GPH 250 PSI
    PID Display for Arch Temp.
    Chumlee of the trader

  5. #5
    Join Date
    Mar 2016
    Location
    Washington County NY
    Posts
    55

    Default

    Try to plug in something else like a drop light , then try your pump.

  6. #6
    Join Date
    Mar 2015
    Location
    Alcona County, Michigan
    Posts
    1,134

    Default

    Quote Originally Posted by Austin351 View Post
    The pump isnt even trying to move, it's not even loading the generator. Agree that my generator does t like the pump but, the start up of the pump is less than the grinder that worked fine.
    That is weird, but no reaction at all from the generator means a cord or plug issue is most likely the cause. If it isn't a connectivity problem, does this pump have a starting capacitor? Some do. It's a little metal can with a wire lead usually located in the terminal box where the cord connects. It might be sensitive to the generator, but that seems like a long shot.
    CE
    44° 41′ 3″ N

    2019 -- 44 Red Maples - My home and sugarbush are for sale.
    2018 -- 48 Red Maples, 7 gallons
    2017 -- 84 Red Maples, 1 Sugar Maple, and 1 Silver Maple , 13 gallons
    2016 -- 55 Red Maples, 8 gallons
    2015 -- 15 Red Maples, 6 Birches - 3+ gallons maple syrup
    An awning over my deck is my sugar shack.
    An electrified kitchen sink and an electrified steam table pan are my evaporators.

  7. #7
    Join Date
    Mar 2016
    Location
    Winter, Wisconsin
    Posts
    138

    Default

    Generator didn't know it was there! Plugged another device in there and when the generator pulled down, plugged the pump in and all is good.

  8. #8
    Join Date
    Mar 2017
    Location
    Toronto, ON
    Posts
    1

    Default

    I think not.
    Life is Good

  9. #9
    Join Date
    Mar 2017
    Location
    Fitzwilliam NH
    Posts
    30

    Default

    Seems a bit obvious I know but is there a chance that it's tripping the gfi on the generator. Try multiple receptacles also, sometimes the blades can get worn out in the receptacles if it's a well used gen or pump cord end, possibly making a bad connection on there and not on the wall plug you tried it on. Like was mentioned already too try simply moving the cord around to see if there is a loose connection anywhere. It doesn't seem like an issue of overload, more a connectivity issue. Just my 2cents!
    2018 Same shed/sugar shack. Same barrel stove , with an upgraded 18”x 24”x 6” pan, a preheater and blower
    22 (very productive) taps on buckets

    2017 Home made barrel stove set up with 2 SS serving trays, in a 12x16 shed/ sugar shack, 14 buckets and 2 gals made. We’re Hooked!
    A 32hp Yanmar Cub Cadet EX 3200, Back Saver

    2016 Turkey Fryer and wood stove outside, 6 buckets, 0 gals and a story!

  10. #10
    Join Date
    Mar 2016
    Location
    Winter, Wisconsin
    Posts
    138

    Default

    Still the same scenario, has been since I last posted. I've tried different outlets, is not tripping breaker. Tried plugging in the pump with and without generator running. It will not pump unless I plug something else in. Once the pump starts running, I unplug the other. Whatever it is, whatever the process, it is working for me.